7702 gateway setup

serial settings: how to determine baudrate?
how to determine character format? no parity, parity? 2 stop bits, or?
Ethernet settings?
port number 502 for default?
Ip authentication? this is the address we want the gateway to connect to, yes?
and what is mask? subnet?

Hello,

You must know all of this information from your network and Serial setup. We cannot know for sure what baud rate, IP address and other settings would work as they are specific to your application. 502 is usually the correct port, as this is standard for Modbus TCP.

For the Baud rate and serial settings I would check with the vendor that sells the Modbus RTU/ASCII device.

For the IP address and Ethernet network settings, please check with the local IT department at your site.

Best regards,
Nick