AB7028 - DRT Flow Totalizer

Hello, i just started to use Anybus Communicator recently
I want to use this AB7028 to get data from a custom RS232 device (a DRT Totalizer) then translate to a Modbus TCP (Flexy 205)
I have set up the AB7028 followed this video How to connect a serial RS232 device to PROFIBUS using Anybus Communicator - YouTube
But it turned out only 2 bits are read


Here are the AB7028 setting



Here is the frame i got from DRT Totalizer by a terminal software

This is the manual of the DRT Totalizer i wanna get data from, in case you need
manuals-guides-digital-rate-totalizer-manual-led-micro-motion-en-64264.pdf (1.6 MB)

Thank you for reading this :slight_smile:

Hi, can you confirm that my settings for consume and produce is correct or not?
i want to read 178 bit data and send a bit data with value of 10

Hello @PhiNguyen,

Try increasing the message delimiter for the subnetwork, I am guessing you are only seeing the last two bytes since the other characters are being seen as separate messages and are being over written.

@PhiNguyen,

Did this do the trick for you?

Deryck