AB7318 Anybus Configuration Manage Setup

Hello,

I am looking for help in setting up an Anybus AB7318 gateway to communicate between a Schunk ECM-EZN100-CN-N (gripper) control module and the Ethernet port on a Fanuc robot controller. I tried following the setup video (from
https://www.anybus.com/support/file-doc-downloads/communicator-can-specific/?ordercode=AB7318
) but am not sure if I have setup the device correctly. I’ve attached a copy of the configuration file that I made. Any guidance would be greatly appreciated!

Respectfully,

Gear_Cell_Setup.hcg (2.43 KB)

Hello,

I’m not sure if you uploaded the wrong file but I don’t see any transactions. You will need to setup consume and or produce transactions to read and write data. Take a look at section 4 and 10 of theuser manual for details on setting up transactions.

Regards,
Deryck

A post was split to a new topic: AB7318 to our Fanuc R30iB Plus Mate robot controller

Topic closed due to inactivity.