Replacing an old AB7632 with a new AB7632-F using Rockwell ControlLogix version 16.
Cannot get data through-put.
Keep getting error 16#0128 even though all input and output sizes are the same.
The data chart is all gray.
Any suggestion
Hi Steve,
Can you share your config file (.hcg) and a screen shot of the input/output settings in the RSLogix/Studio 5000 software?
Thanks,
Kyle
here you go
In the Anybus Configuration Manager, can you go to “Save As” to save that file and send it to me please?
tried that, in old versions of RSLogix, Anybus card does not show up after including EDS file, still generic Ethernet module
OK. I see what’s wrong. In RSLogix, you need to change the sizes to 120 and 120, because you have it set to words (16-bit).
Can I change the Anybus Config to 480/480?
Yes, that works too.