Hello everyone,
I have little experience with EtherNet/IP and I need help setting up my AB7671 to interface between a Profibus Master PLC and a EtherNet/IP Adapter remote IO rack.
Thanks,
Mo
Hello everyone,
I have little experience with EtherNet/IP and I need help setting up my AB7671 to interface between a Profibus Master PLC and a EtherNet/IP Adapter remote IO rack.
Thanks,
Mo
Our office is closed for the day (5pm EST), but here is the link to the documentation:
https://www.anybus.com/support/file-doc-downloads/x-gateway-specific/?ordercode=AB7671
Please read the Network Guides and Application notes, and let us know if you have any specific questions we can help with. All software and configuration files are available for download on that page as well.
Hello Bob, the unit’s serial number is A039FDBD.
Thanks,
Mo
Thanks for replying @kyle_HMS. I need to know what to enter in the gateway’s scan list to make it communicate with the 1794-AENTR adapter.
The ethernet scanner is going to read the memory locations on the ethernet adapter (slave). You will need to know the memory locations and sizes of the data you want.
Here are the instructions for setting up the Scanner as found in the Network Guide.
You will need:
Thanks for the reply @kyle_HMS.
I’ve already looked at the documentation and figured out how to do almost everything except for the Connection Points. The problem is Allen Bradley does not offer any documentation or support for connecting a 3rd party controller/scanner to the Flex IO 1794-AENTR adapter. This knowledge base entry confirms that:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/493993
I called HMS before we purchased the gateway and I asked if it supported this particular Allen Bradley adapter and their answer was yes. So I am assuming that you have the information I need to properly set up the connection points for this particular unit in the gateway’s scan list.
Please respond at your earliest convenience. Thank you very much for you help.
I am going thru the EDS now, but please try the 100/150 for exclusive owner as that is common.
This is the exact modules lineup in the rack:
1794-AENTR
1794-OB8EP
1794-OB8EP
1794-OB8EP
1794-IB16
1794-IE8
1794-IR8
I hope that helps.
The EDS is showing:
3, $ O=>T
5, $ T=>O
doesn’t seem right…
Can you confirm that you tried these?
O=>T = 3
T=>O = 5
Yes I confirm that I tried the following:
Originator -> Target
CO Point: 3
Size (b): 4
Offset (w): 0
Target -> Originator
CO Point: 5
Size (b): 4
Offset (w): 2