Hi,

I have the AB7680-F gateway. I have the CC Link working fine on Version 1 4 Stations and can see data in the web based monitor. I am trying to connect to a Keyence CV-X400 camera on EIP. The keyence is set to 20 bytes as is the gateway but I can’t figure out the connection settings.

pic1 pic2

I am new to setting up HMS gateways and can’t see how to get the Keyence EDS file if that is even possible! Any help would be appreciated

You will need to get these settings (connection points, transport type, etc.) from Keyence, either from their EDS file or contacting their support.

https://www.keyence.com/support/user/cv-x/manual/index.jsp

1 Like

All sorted, read the EDS file wrong, thanks for the pointer!