Between Allen Bradley (Ethernet IP) and Mitsubishi (CC link IE)

We need to transfer data back and forth between Allen Bradley (Ethernet IP) and Mitsubishi (CC link IE). We cannot get it working even though we used the eds file from the website. There is always a fault, even after disabling keying.
When all data was set to 512/500/496/400/20/0 bytes, the module always had a fault.
We haven’t had the Allen Bradley side fixed and haven’t looked at the Mitsubishi side yet.
The EDS created tags with 500 inputs and 496 outputs.

Allen Bradley Details are as follows
Type : 1756-L73S Guardlogix 5570 Safety Controller
Revision : 28.011

Studio 5000 details are as follows
Version : 28.03

Mitsubishi details
Q61P
Q06UDVCPU - CC-IE card
QJ71E71-100

HMS - Anybus gateway details

Anybus Issues.docx (1.35 MB)

Hello Martin,

It looks like you are using the wrong eds file for the device.
You can see here you are using one for our Serial linking device. image

It looks like you are using an AB7956. You should be able to use the eds off of the files and documents page for that device.

Once you re-add it with the correct EDS you should be correct. Make sure you add it using the IO size you have configured though Anybus Configuration Manager.

Regards,
Deryck