Bridge config

Hi everybody i’ve a problem with Anybus Wi-Fi config… my goal is to connect Siemens PLC with RJ45 to bolt and bolt to an AP and be able, at the same time, to reach Siemens PLC at 10.100.3.40 and Bolt in http at 10.100.3.104… is it possibile? and if yes how is the bridge mode? Thanks in advance

Hello @andre69,

You should be able to accomplish this with the bolt. You need to ensure the network it is connecting to will allow this to work. Keep in mind the bolt is not a gateway so the IP address needs to be in the same subnet.

Bridge mode only work with two Anybus wireless devices. For this setup you will want to use layer 2 mac clone mode and enter the PLC’s MAC.

Deryck