Can not connect to SLC 5/03 when using Cosy 141 as a gateway

I have other PLC’s on other ewons that work fine. But for some reason I can not connect to thi sPLc through the ewon gateway. The ewon gateway is set to 9600,NO, CRC, 1. These settings match the RSLinx settings. But I can not access the PLC.

Any help is appreciated.

RSLinx should be using the Ethernet driver. Are you sure you have this PC configured like the other ones that work?

I discovered the issue. The DIP switch was not pushed completely pushed over.

You can close this ticket. Thanks.