there are several possible reasons:
TIA Portal: Device configuration
- CANopen Manager auto configuration: must not be activated
TIA Portal:
- a running SDO command from the PLC
all running SDO commands must have been completed and a new one must not be started when the configuration shall be downloaded to the CM CANopen
ERR LED of the CM CANopen:
single flash: CAN Controller: warning limit reached
Possible reasons:
-
check if the CAN bus is terminated correctly:
see manual of the CM CANopen: chapter 4.4 Line Termination
note:
there must be exactly 2 resitors with 120 (5%, 1/4 W max.)
-
there is not a connected CANopen device
-
CM CANopen and the other CANopen module(s) have reached warning level set
note: power on
the time of the CANopen initialization after power on until the device has started its CAN Controller depends of the module
when this time is too different it can happen
that the fastest module has entered warning level reached before another device has started its CAN controller
=> it depends of the CAN controller if it confirms the successful reception of a CAN message or not when in warning level reached
so the bootup message of the next device will not be configrmed and the device will also enter warning level reached
so each one is waiting for a confirmation and the processing is stuck