Communication Help With AB7013-C

Good Afternoon,

I have a AB7013-C connected to a siemens 1517F-3 PLC over profinet. The problem I am having is I cant see the module in IP Config (V4.1.0.0). I have manually added a rule in windows firewall settings to allow all ports already and still have nothing. Wireshark is showing no data at all to the module, at first I thought the module may be faulty but i have tried the other two we have on the shop floor and I’m having the same problem.

Has anyone come across this before?

Best Regards

James

Hello @Morgan_Automation,

I am not sure why IPconfig isn’t finding the device, does it work if you disable the firewall? In any case you should not need to use IP config with a Profinet device. I would recommend you set the device up using TIA portal and assign a device name then an address to that. You will need to do this anyways to setup the device.

I recommend taking a look at the application notes on the devices files and documentation pages. https://www.anybus.com/support/file-doc-downloads/communicator-specific/?ordercode=AB7013

Hi Deryck

I have tried the Tia Portal route but its not displaying an as an accessible node in there either, cant even see a Mac address.

Regards,

James

Have you downloaded a configuration with ACM yet? without one the device will not start and will not show up on the network.

Deryck

Hi Deryck,

Excuse my ignorance as i’ve not used many HMS products before but whats ACM?

Regards,

James

Hi @Morgan_Automation,

Sorry I used the acronym with out thinking. ACM is Anybus Configuration Manager. It is available via the files and documents pages for any of the devices that use it. https://www.anybus.com/support/file-doc-downloads/communicator-specific/?ordercode=AB7013

You will need to connect via the serial programming cable to the device.

Regards,
Deryck