Hi,pls let me know maximum modbus commands supported in the
Anybus communicator. Please share range Limitation document for reference.
There is a limitation of up to 150 transactions (or 75 commands) where each query or response is considered a “transaction” (i.e. produce/consume).
Kyle
Thank you for your prompt reply.
As I can configure up to 55 commands only.
I have created AB7072 application, in which 13 Modbus Slave nodes are configured and in
each node having 4 commands (READ command#1 400001&2 ; #2 400100 to 101 ; #3 400200 to
201; #4 400300 to 301.
Actually I want to connect 22 Modbus Slave nodes with 4 commands for each node.
BR
There is a limitation of up to 150 transactions (or 75 commands) where each query or response is considered a “transaction” (i.e. produce/consume).
You may need to use 2 Communicators in this case.
Hello Kyle,
I appreciate your speedy reply.
I have noted your points and use two ABC for this application.
Stay safe and Take care!
BR
kyle_HMS
HMS Technical Support
June 1
There is a limitation of up to 150 transactions (or 75 commands) where each query or
response is considered a “transaction” (i.e. produce/consume).
You may need to use 2 Communicators in this case.
Visit Topic or reply to this email to respond.
In Reply To
prash
June 1
Thank you for your prompt reply.
As I can configure up to 55 commands only.
I have created AB7072 application, in which 13 Modbus Slave nodes are configured and in
each node having 4 commands (READ command#1 400001&2 ; #2 400100 to 101 ; #3 400200 to
201; #4 400300 to 301.
Actually I want to co…
Visit Topic or reply to this email to respond.
To unsubscribe from these emails, click here.