Cosy LAN side

I’m looking at using an EC61330 or EC6133C in a small water treatment plant that has two different filtering skids. These skids are not on the same subnet. Can I set up the LAN ports for two different networks? i.e. 192.168.15.0/24 and 192.168.100.0/24.

Hi Rob,

No, the LAN can only be set to one IP. You could use 192.168.xxx.xxx for a subnet if you are not using 192.168 for your WAN connection. it will be a large network but then you could access both from the Cosy. otherwise you would have to update the IP address whenever you need to view the other, or put a device on one of the skids that will NAT the IP addresses to the subnet the cosy is using.