EN2SE-R Ethernet/IP Connections


#1

Hi we are testing out using an EN2SE-R to connect a new ControlLogix PLC (Ethernet/IP) to an older SLC-5/04 (serial DF1), but we want to also connect an RSLogix500 engineering station (for programming the SLC) and a Red Lion DSP (for data collection from the SLC) on the Ethernet side of the EN2SE
Can the EN2SE-R be configured to allow these additional Ethernet/IP connections through to the SLC via the DF1 serial subnet?


#2

There can only be one Ethernet/IP connection to the EN2SE-R, your Allen Bradley PLC and it cannot act as a transparent gateway. It is an I/O device.

You can have several DF1 slaves on the serial side using RS4XX.