No, im reading Data Memory area.

I am still waiting to hear back from Omron, I sent them projects to look at.

I believe I have tested all these combinations:

  1. 1 , 1 , IP
  2. 1 , 0 , IP
  3. 0 , 1 , IP
  4. 1 , 250 , IP
  5. 0 , 250 , IP

Do I need to restart the eWon or should Update then Init work to restart the FINS?

I’d recommend reading the status tag for the initial tag just because then we don’t need to worry about if we’re reading the correct area and can just focus on the FINS path. I believe after you hit the update button and the initialize button you should be ready to go

Seems happier with Status, but no matter what I have in Fins, this always shows 0.

Status = 2 if I add 1x data read.

If we’re able to read the status tag on the FINS IO server than that means we’re at least able to communicate with the device. If that’s the case I’m thinking it may be an issue with how you’re addressing the new tag

I got word from Omron that FINS is only available on Ethernet Port #2

I will report my test results. Thanks for your help so far.

Testing went well. When talking to Port 2, it worked fine. I also found that all 3 of the above settings worked.

image

Thanks again for the response.

I tested on Firmware 13.3s0

image

Thanks for the update @jonmsi

glad to hear that you got the device working!