Flexy and PLC Connection


#1

sir, and for the connection wiring scheme between the eWon and the M221 PLC what use as cable? can you send me a detailed wiring diagram

Thanks


Connexion avec ecatcher
#2

Here is are documentation on setting up a Schneider PLC.

https://websupport.ewon.biz/support/product/flexy-plc-schneider/schneider-1


#5

Hi,

thank you, I made the local connection of the controller with the eWon, I entered my values of variable, I am doing the supervision interfaces with viewOn, for the LEDs I want to do the sycronisation with the PLC and I tried with the animation function, it did not work ,

can you help me

Thanks,


#8

how can i associate tag to viewon object (i.e. symbol colorspot to show status of boolean tag) or change previously associated tag at runtime using basic script.
plz guide me on this.


#9

You will have to import your tags from your device found on page 8 of the following document. For setting up animations with the tags you can refer to section 6 of the same document.


#10

hi ,
thanks
I’ve already imported tags and done animation but I want the light to be in real time with the eWon


#11

What lights are you wanting to be in real time? How fast are you trying to make these changes?


#12

indicators, lights, 500ml second


#13


#14

The Flexy does close to real time. Since your reading off the Flexy then having an animation happen after the read there will be a small delay.