Flexy rs485

I have a Flexy 205 and a 2 serial port card FLA3301_00_/s
Should I be able to read a sensor communicating via Modbus RTU via RS 485 ?

Hi,

If you are using RS485 then the first port, s1, can have its dip switch configured for RS485 with termination or RS485 without termination.

As for the Flexy it will support Modbus RTU via RS485 when it is configured as the master. The Modbus IO server can be used for this.

ok, so how do I declare that in the Modbus IO server?
Com port # , e.t.c

Or do I need to use some Basic IDE scripting to retrieve values at modbus addresses?
Any tutorial or something on this topic would be very helpful.

You should be able to setup the modbus IO server and create tags on the flexy that will read the addresses. here is the document on modbus RTU using the io server.