HMS-EN2MB-R set up modbus


#1

HI
HOW TO READ SIEMENS PAC 3200 ENERGY METER DATA ,MODBUS ADDRESS FOR TOTAL KWH. ITS GIVE ME ERRORsiemens meter pac3200.pdf (6.8 MB)


#2

What is the error?

Have you read the manual?


#6

Hi Kyle

If I check the transaction it gives the following error, please tell me the how to read the Siemens PAC 3200 address for total KHW


#7

You need to show me the command you are using or export the config file for me.

Are any other commands working?

What is the offset of the register you are trying to read?


#8

Hi kyle
I have read the manual and setup my HMS-EN2MB-R with Siemens PAC 3200 energy meter, and now I want to read the register 1 ,but it gives me error


#9


if I put 100 in starting register than the meter communicate and gives no error


#10

I think you need to start at 0. Like 40000.

image

Offset 1 in the manual = 0 in the Anybus


#11

if I put 100 in the register field it gives me no error


#12

ok you mean if I want read Voltage V offset 1 then I have to set the starting address in any bus 40000 and element 1


#13

Yes correct. You may also need to change the ‘Data Encoding’ field to get the proper byte swapping if the numbers do not come out right. Is it working now?