HI
HOW TO READ SIEMENS PAC 3200 ENERGY METER DATA ,MODBUS ADDRESS FOR TOTAL KWH. ITS GIVE ME ERRORsiemens meter pac3200.pdf (6.8 MB)
Hi Kyle
If I check the transaction it gives the following error, please tell me the how to read the Siemens PAC 3200 address for total KHW
You need to show me the command you are using or export the config file for me.
Are any other commands working?
What is the offset of the register you are trying to read?
Hi kyle
I have read the manual and setup my HMS-EN2MB-R with Siemens PAC 3200 energy meter, and now I want to read the register 1 ,but it gives me error
I think you need to start at 0. Like 40000.
Offset 1 in the manual = 0 in the Anybus
if I put 100 in the register field it gives me no error
ok you mean if I want read Voltage V offset 1 then I have to set the starting address in any bus 40000 and element 1
Yes correct. You may also need to change the ‘Data Encoding’ field to get the proper byte swapping if the numbers do not come out right. Is it working now?
Hi kyle
After Setup my HMS-EN2MB-R ,I am successfully read the IP address of the meter through register 630002.
but if I want to read the line voltage Va-n,.as per the manual the address is 1, so how to read the address through HMS, I have tried 40001 & 40002 but its showing illegal data error.
Try read input registers 30001
Topic closed due to inactivity.