I received a the following support request from sales:
I have an HMS-EN2SE-R linking device. I am trying to configure inside a compactlogix controller and control Oriental Motors Steper Motor Drivers. I having an “invalid input size” error. I need help with getting this application started and configured.
When you are seeing this error with a linking device this typically means the configuration in studio 5000 does not match the configuration on the linking device. Re-downloading the configuration to the device and make sure you apply the changes to the studio project and update the module definition. This should clear up this error.