How to enter the IP address of my Mitsubishi PLC in I/O server

Hi

I need to set up a eWon for my Mitsubishi Q03UDECPU. Please see below picture . I am not sure what to set after the IP address ?

Can you explain what is after the IP address ?

Regards

THe format is as follows:

QCPU,<Protocol TCP/UDP>, PLC IP Address, Port Number, 0, 255

The Port number for Mitsubishi communications is required for communications.
0,255 is used for all Mitsubishi communication, and required for machine protocol.

Thank you for the fast response