You need to use the DF1 IO Server and connect with the DF1 serial cable. Can you send a screen shot of your settings?
Here are the channel 1 settings but from what you are saying we can’t communicate over this channel using the ABLOGIX driver?
If we enable Modbus TCP on this channel, could we use the Modbus IO Server?
Thanks,
Chris
Yes, but you will have to use Modbus addressing.