Modbus diagnostics

@KY2020
Hi Kenneth,

In regards to your question:

"We are using HMS-EN2MB-R to communicate with Honeywell Slate Modbus TCP to our ControlLogix L73 PLC.

Is there a way to detect the modbus communication not working / freezing.
We had this happen a few times and we couldn’t detect it. We had to turn and off the HMS in order to communicate with the Slate again."

I would take a look at the section in the User Manual that deals with the Control/Status Word, Live List, and Transaction Status List. These allow you to retrieve the status of the device over the network and could be used to alert you if something was wrong:

Please let me know if you have any questions about it.

Kyle

Hi Kyle,

Here is what I have now for comms with the Slate:

If I add the control/status word will it shift all my registers?

Below is the tag in the PLC

I plan to use the ConnectionFaulted bit for lost comms with HMS and the PLC as an alarm.

Thanks,

Kenneth

Yes, if you enable the control/status word the registers will automatically shift to allow space for the word.