Hi kevin
I will share the backup, before that i wanted to give some information about the issue…
Our 13 slave device setting (Not working )
Baud rate- 9600
Parity-No
Stop bit-2
Data bit -8
Working 2 device setting in same bus
Baud rate- 9600
Parity-No
Stop bit-1
Data bit -8
RTU Master setting
Baud rate- 9600
Parity-No
Stop bit-1
Data bit -8
In our 13 not working devices, Earlier there was only 4 slaves with same setting. it was working and we have added extra 9 slaves to the same bus , after all 13 slaves no communication. All time two working devices was in place…
Some time RTU master nearest slave devices are working
Total RS 485 BUS length around 300 meters
All devices connected daisy chain
Used 1 pair sheilded cable not twisted (polycab)
No termination and voltage bias resister in the bus
Slave device have signal ground. port not connected only + and - Connected