Negative Tag values in from modbus, ViewON Glitch

@anonqslaxkvo
Hi Dale,

Let me know if recreating that tag and those numbers helps.

Thanks,

Kyle

  • Issue with negative numbers showing up as larger positive ones
  • Fixed by appending I (making signed) in tag address field in flexy
  • Has one tag stuck on DWORD, can’t change, will try to recreate tag and see if that fixes it
  • Issue with the caution (yellow triangle) flashing in Viewon
  • He will recreate the element to see if that fixes it

https://forum.hms-networks.com/user_avatar/forum.hms-networks.com/kyle_hms/45/4563_1.png

kyle_HMS HMS Technical Support
April 19

@anonqslaxkvo
Hi Dale,

Let me know if recreating that tag and those numbers helps.

Thanks,

Kyle

· Issue with negative numbers showing up as larger positive ones

Item fixed by adding an I to the Modbus address

· Fixed by appending I (making signed) in tag address field in flexy

· Has one tag stuck on DWORD, can’t change, will try to recreate tag and see if that fixes it

Deleting and recreating the tag fixed the issue

· Issue with the caution (yellow triangle) flashing in Viewon

· He will recreate the element to see if that fixes it

Recreating the element did not fix the problem

https://u5094295.ct.sendgrid.net/wf/open?upn=iM7ajgtlA1x8smCiUohtSDD3ejb8-2FvxY5EaccUOOjH5QucdMwd4VNrNUKTYyZfDBNWZDmqiMTuFvG-2FgnlVNVDwUVbm8kL79KR65tRYp-2FyKbgO-2FtoEBsqtQo-2FMBMavtzi1kdSl85wxagWcmqW5ppYOahHPz7M67rq2IvTmfti3pHyLEF4VMe1Bjx77Oh-2Buu9B7kWUNCkXidVkmQeUlkdkH-2B8ZSnjf84muMLWzZC7Ab0I-3D

Kyle,

I found the problem with the warnings. There was a ghost text behind the one showing.

Dale