Do you have a solution to connect EtherNet/IP devices to a PROFINET S2 redundant controller?

I think they are asking for Single-Channel Switched. This only requires one physical RJ45 but it would allow a connection to the Primary and a Secondary connection. The firmware must determine which connection is controlling the outputs (Application Relationship, ARa or ARb).

Hello,

The AB7670 would work for this application as the gateway interface is a Profinet Io device/slave. However there is no redundancy built into the Gateway itself.

https://www.anybus.com/products/gateway-index/anybus-xgateway/detail/anybus-x-gateway-ethernet-ip-scanner---profinet-io-device

Let me know if you have any questions.

Thanks,

Rob