Setting Up Multi Register Block

Hi:
I am setting up a new genset controller, Kohler DEC 550, and am using my own template for registers. This controller has what is called an event stack, which reports as many as 254 events, read from 16 consecutive registers which must be read as a block. The bit numbers from those 16 registers correspond to a numeric event code, which corresponds to a particular event listed in a table, see below.
Event_stack_1
Event_stack_2


How can I set this up properly? I don’t need to have access to every one of the event codes.
Thanks,
Robert

Hello Robert,

With the way the reads directly correspond to a parameter in Argos the Netbiters do not have an option for a read multiple request. If they need to be read as one read multiple the device might not be compatible with the netbiter.

Deryck