Hello!

I have a cpu319-f of siemens and I want to connect with ANYBUS AB7649-F, but it is impossible, the name is correct but the communication is not possible

How can I configure it to communicate?

Thanks!

Why do you think this is impossibe?

We have two examples on the AB7649 Product Page under Application Notes which explain how to connect with a Siemens PLC. The required GSDML file is on the same page.

Hello Kyle!

I try that and I don’t get it

I have this communication in the PLC

And the configuration of the Anybus I know if that’s fine

Or this way

Thank you very much for your help

Hello!

I have this

and I can´t communicate

Did you install the GSDML file in the Siemens program?

What are the status LEDs doing on the gateway?

This is the status LEDs

And I have this GSDML file
image

What is the serial number of the gateway?

You need to use the new Anybus GSDML file. The one you are using is an older version. It’s on the product page and I also created a link above.

Perfect! It is communicate!

Now how do I know if I write the outputs well?
I use the function SFC15 and with the web can I see if the outputs are activated ???

image

image

This page just shows the first few dozen registers in the gateway’s memory, so if you write to those you will see the values here.