Hello!
I have a cpu319-f of siemens and I want to connect with ANYBUS AB7649-F, but it is impossible, the name is correct but the communication is not possible
How can I configure it to communicate?
Thanks!
Hello!
I have a cpu319-f of siemens and I want to connect with ANYBUS AB7649-F, but it is impossible, the name is correct but the communication is not possible
How can I configure it to communicate?
Thanks!
Why do you think this is impossibe?
We have two examples on the AB7649 Product Page under Application Notes which explain how to connect with a Siemens PLC. The required GSDML file is on the same page.
Hello Kyle!
I try that and I don’t get it
I have this communication in the PLC
And the configuration of the Anybus I know if that’s fine
Or this way
Thank you very much for your help
Did you install the GSDML file in the Siemens program?
What are the status LEDs doing on the gateway?
What is the serial number of the gateway?
You need to use the new Anybus GSDML file. The one you are using is an older version. It’s on the product page and I also created a link above.
Perfect! It is communicate!
Now how do I know if I write the outputs well?
I use the function SFC15 and with the web can I see if the outputs are activated ???
This page just shows the first few dozen registers in the gateway’s memory, so if you write to those you will see the values here.