Hello. I,I’m new to ewon
A counter 100 to 200 is generated by arduino which via UART transmite it.
The physical medium of transmission is RS 485
I want to read this counter at EWON FLEXY 201 with a FLA 3301. This module was configurate.
My issue is:
how do I configurate los I/O services and how create the variable to see the counter?
Thanks
Hi Carlos,
Are you trying to read raw TCP data over a serial connection or is the arduino capable of transmitting in a protocol such as Modbus?
If it’s a raw TCP connection, I’d recommend taking a look at the pages below
I would try creating a vcom (virtual communication) port using our evcom software.
Software download:
Manual:
Hello Tim
Firts of all, Thanks for your self
Yes, the arduino can use the protocol modbus RTU (it`s the protocol which I use ,but before I will use in further projects), but before I need to make tests with the protocol I told you about.
Thanks for all
Ok, in that case you should just need to go into this section
then make sure all of the serial settings match up for the arduino and you should be able to poll modbus addresses
Ok thanks
I generated the modbus in arduino
The questions : Does Ewon work only master with Modbus RTU?
How do i configure the FLA 3301 To RS 485?
Thanks for information
It looks like we’re not able to act as a Modbus RTU slave, but we can do the following:
Take a look at page 8 of this document to change to RS485
Ok thanks for all
You’re welcome, did you have any other questions?
Hi Carlos,
it looks like you may have deleted the Init and Cyclic sections. Try deleting the BASIC IDE section here:
Then try writing your code in the Init section
That is the solution to the problem
Thanks for all
You’re welcome, let me know if you run into something else with this