Trasmit PDO to

Hi All,
I have an anybus X Gateway Canopen AB7307 configurated as master.
On the CANopen network there is an inverter schneider LXM32A and on the Profinet network there is a PLC siemens S71500.
I’ve configurated the network with Anybus Configuration Manager - CANopen and the PDO Mapping for trasmitt and receive the data.

image

I need to write the register 6060 but there is not such register inside the PDO Mapping menu.
I find it instead inside the Object Dictionary menu.

How can the PLC write that register?

Thanks,

Marco

Hello,

This gateway does not support SDO requests during run time, so if this parameter is not PDO map-able you will not be able to access it from the PROFINET side. I might suggest asking the vendor if they have a workaround for making it map-able.

Best regards,
Nick

Hello,
if schneider don’t have a workaround for making it map-able what is possible to solve the problem?
I change the anybus model ?

We do not have an Anybus gateway that supports SDO transfers. We do have a device that connects to S71200 PLCs that supports SDOs, however this does not work with the S71500.

I apologize for the inconvenience,

Nick