Anybus Modbus to BACnet gateway for Modbus TCP to Bacnet IP

I have questions about the Anybus Modbus to BACnet gateway.

  1. Is it possible to have a Modbus TCP input converting to a Bacnet IP output?
  2. How is the configuration done? Through a web browser?
  3. Is the Anybus Configuration Manager a software that has to be downloaded to a PC?

Thanks in advance.

Yes, the Anybus polls Modbus servers and provides that data to the BacNET network.

I assume you are referring to the Anybus AB9900. The configuration is done with the included ABC-MAPS software, which runs on Windows and is a very lightweight software. You download the configuration from the PC to the AB9900 using a USB cable. For more details, check out the User Manual.

I have the Intesis INBACMBM1000000 gateway.
To confirm, is it possible to use both Modbus TCP and BacnetIP at the same time on this model?