We have an Automation Direct Click PLC C012DD2E-1-D in our control panel. Is it possible to connect the Click PLC to Profibus using an Anybus AB7832-F X-Gateway so our customer can communicate with the panel for control and status?
Thanks, Bill
Hi,
We have an Automation Direct Click PLC C012DD2E-1-D in our control panel. Is it possible to connect the Click PLC to Profibus using an Anybus AB7832-F X-Gateway so our customer can communicate with the panel for control and status?
Thanks, Bill
Hi @WDau,
It looks like the PLC supports Modbus TCP and Ethernet/IP, so you could use either one to connect to the AB7832 and exchange data with the Profibus network. You will want to refer to the Network Guide - Ethernet Slave on the Product Download page for instructions on both Modbus TCP and Ethernet/IP.
Kyle