CIP Safety over wireless, fault code 32

Using (2) bolts in a AP/Client scenario. Layer 2 bridge. Compact Logix L320 talking to remote safety I/O.
RPI rate at 300ms.
Using DCS function blocks with a a discrepancy time of 2000ms.
Every 3-5 hours the function block returns an error code 32.
Error Description: The Input Status input transitioned from ON (1) to OFF (0) while the instruction was executing.
Corrective Action: Check the I/O module connection or the internal logic used to source input status.

Hi @kevinromer,

I guess to start with, can you confirm that the bolts are on the latest firmware?

https://www.anybus.com/support/file-doc-downloads/wireless-bolt/?ordercode=awb2030

I am running 2.00.12 [14:42:28,Dec 13 2019]

Could we use wireshark and try to capture when this error occurs to help debug this?