Communication of OPC ua io client with kepware OPC server

I’m using ewon flexy 202.
I’m trying to connect it using OPC ua io client to kepware OPC server.
Certificate transfer done using FTP.
But no communication

Hello Ragesh,
Please update your Flexy firmware with latest version. Also ensure to set value as 1 for ‘OpcuaIOSrvlgnCertErr’ parameter s shown in the pic.


-Prashant

Yes. I did update firmware. Now it’s communicating but network time out error is there .
Checked in event log and found
Reboot reason watchdog in progress (opcuacom)

Hello Ragesh,
Have you updated sys parameter ‘OpcuaIOSrvIgnCertErr’ setting in your Flexy configuration?
-Prashant

Yes I did. Now it’s resolved thank you.

I have another query .

Hope you can help.

I want to generate time delay for Alarms.

Condition is if my machine speed below set point more than 10 minutes then SMS to operator
More than 20 minutes then SMS to supervisor
More than 30 minutes then SMS to IC maintenance.

If Speed reached to set before this then timer will reset.

I tried ontimer but it’s not working

Hello Ragesh,
Thank you for the confirmation. Please share your Flexy application [backup] for further analysis.
-Prashant (https://hmsnetworks.blob.core.windows.net/www/docs/librariesprovider10/downloads-monitored/manuals/knowledge-base/kb-0135-00-en-create-an-ewon-backup-through-ebuddy.pdf?sfvrsn=51dd4bd7_11)

MOVED TO STAFF NOTE (49.5 KB)

Hello Ragesh,
I had discussion with our distributor engineer, who has co-ordinate with you for further resolution.
-Prashant