DK-RC-BAC-1 Easy IO FG20+ BacNet commands not updating temp values on box

Hello,

Per our conversation, you have a DK-RC-BAC-1 unit that is connected with a EASY IO FG20+ PLC unit. You are experiencing issues with the PLC, that when it sends a set temp command the temp does not update.

However, this commands send no problem from the HMI and remote.

Can you please supply the dipswitch summary? I will reach to SPain for some additional guiddance on the issue.

Dip Switch Summary

SW1
Lo Lo Lo

Sw2
hi hi lo lo lo lo lo lo

Sw3
hi lo lo lo lo lo lo lo

Sw4
lo lo

Issue resolved,

They needed to adjust the Occupency difference by 5 degrees. Updated development for their testing on required diffrence.