Flexy 201 and ISOTCP with Siemens S7-200

Hi,
We have a customer with a PLC Siemens S7-200, CPU224 and a card Ethernet CP243-1.
He use a Ewon Flexy201. (11.2s2)

He have read the documentation of your website about the communication between them with ISOTCP.
aug-049-0-en-polling_data_registers_from_siemens_s7-200_plcs.pdf
aug-018-0-en-s7-200_ppi_multimaster_remote_connection.pdf
aug-017-0-en-s7-200_ppi_monomaster_remote_connection.pdf

The customer have had an error when he have configured the IOServer S7200 on Ewon.
Impossible to finished the configuration.
He have tried the IOServer S73&400 and this IOServer have worked with his PLC S7-200.
Why the IOServer S7200 did not work with his PLC S7-200 ?

It seems that the Ewon gives a error on the COM (serial COM ?).
The Flexy201 doesn’t have a serial COM.
The communication must to be on Ethernet LAN.

When he ‘apply’ on the IOServer S7200 page, Ewon gave this error :
The error : ERROR: Invalid COM port number specified

I send you pictures…

Thank you for your help,Flexy_S7200_ISOTCP_ERROR.pdf (325.7 KB)

Rémi Nolin

Hello @RemiNolin,

It looks like there could have been a serial card installed when the server was initially configured. You should be able to press the Clear button to reset the settings. You will then be able to reconfigure the IO server.