Flexy tagging on a Beckhoff PLC

Hi,

I have a client who is wants to use the tagging functionality of the flexy for things like alarm notifications and historical tracking with a Beckhoff PLC. Do you have any experiencing pairing the Flexy with a Beckhoff? What is the best
way to do the IO server on the flexy?

Any information would be helpful. Thanks.

Hello,

Your best option will be to set up the PLC to publish PLC tags and then use the modbus server on the Flexy.