Hi,
HMS-EN2MB-R MTCP is flashing RED when Modbus device is not powered On.
But the HMS-EN2MB-R still alive without error Studio5000.
Can I get the MTCP status in my ladder logic?
Or I have to program an watchdog bit with the device?
Thanks
Hi,
HMS-EN2MB-R MTCP is flashing RED when Modbus device is not powered On.
But the HMS-EN2MB-R still alive without error Studio5000.
Can I get the MTCP status in my ladder logic?
Or I have to program an watchdog bit with the device?
Thanks
Hello @fredpou,
You can see the status of the modbus side by enabling the Live list. See section 1.8 of the user manual for detail. The Live list will show you the status of each trasaction and would be showing errors at the same time that you see the MTCP flash red.
Thanks
Envoyé de mon iBidule✉