IN485UNI001|100 Taking down Bacnet MSTP Network

This unit seems to be taking down the Bacnet MSTP network. We can take it off and tie the wires together and it comes back up. There are 3 more of these devices on the same network wired the same way and they are working fine. Any Suggestions?

Thank you,

Hi @wilcoo,

It sounds like you need to increase the Max Master setting to 127. You may be able to do this with your BACnet control system, or you can follow the instructions below to configure it using YABE.


BACnet MS/TP devices that cannot be configured with MAPS, the devices can be configured with the BACnet explorer program, YABE.

PLEASE NOTE: HMS Networks doesn’t own YABE software and doesn’t support it, this document is intended as a guide.

APPLICABLE PRODUCTS

Intesis BACnet MS/TP Devices

PRE-REQUISITES

Intesis BACnet MS/TP Device

Windows PC with YABE installed

USB-to-Serial Adapter for PC

Installing YABE

YABE can be downloaded from Yet Another Bacnet Explorer download | SourceForge.net. A USB-to-Serial converter should be connected to the BACnet MS/TP port on the Intesis Device. In YABE, clicking the + icon will add a new device. This will open a window where the correct COM port and serial settings can be set. Then YABE will scan to find the Intesis Device.

Using YABE

YABE is a BACnet explorer, but can also be used to configure BACnet settings, like ‘Max Master’:

Another example is changing the BACnet Device Instance Address: