Sorry about that, I will have to look into adding the ability to provide .cfg files here.
One thing I can immediately tell from the log though is that you are not getting any response from the device you are trying to communicate with. Can you confirm you are using Modbus RTU on the subnetwork side?
The following are reasons why you would not see a response from a Modbus RTU slave device,
-You are trying to query the wrong node. In this case you will want to double check that you have the right node selected in your configuration file. In your case this is 1 (from the log)
-There is an issue with the wiring on the serial bus. Depending on the serial interface (RS232, RS485 or RS422) you may just need a null modem or to switch the rx and tx lines.
-There is an issue with the subnetwork serial settings (baud rate, parity, stop bits and data bits).