Hi,
I have a Anybus Modbus to Bacnet, my modbus adress start from 45392 but the anybus says ILLEGAL DATA ADRESS could you help me please ?

Hi @Pipovic,

Just to follow up here what we discussed on the phone, you need to use the modbus address not the register number. you can do this by subtracting the 40001 offset from the register. So 45392- 40001 = 5392

Deryck

Thank you for the support Deryck