Good day, could someone please confirm the following.
AB9005 ModbusRTU slave to ModbusTCP Client will not work
I need ModbusTCP server to ModbusRTU master. As stated below I think that is AB7028? Is that correct?
Thanks!
Regards,
Bob Moser
Good day, could someone please confirm the following.
AB9005 ModbusRTU slave to ModbusTCP Client will not work
I need ModbusTCP server to ModbusRTU master. As stated below I think that is AB7028? Is that correct?
Thanks!
Regards,
Bob Moser
Hello Bob,
Yes the AB9005 would be a Modbus RTU slave.
For a modbus RTU master you will want to use the AB7072. This is a modbus RTU master and a Modbus TCP slave along with a ethernet/IP slave.
You might also be interested in the AB7702. It is a transparent Modbus TCP to RTu gateway. passing request from a TCP master down to an RTU bus.
Best regards,
Deryck
Thank you again Deryck!