Unable to Connect ewon Flexy 201 with the AB PLC Micrologix 1400

Hi,

I am using Ewon Flexy 201 I set the LAN IP and SUBNET for flexy is

192.168.2.102
Subnet - 255.255.255.0

i have connected 2 PLC and 2 HMI with the IP is

PLC 1 - 192.168.2.108
PLC 2 - 192.168.2.111
HMI1 - 192.168.2.109
HMI2 - 192.168.2.112
Subnet for all is 255.255.255.0

When i Ping from cmd prompt when flexy connected to my laptop with the wire i can get ping will all connection

when i disconnect cable from flexy to my laptop and connect flexy with e catcher i can connect to flexy but unable to ping any of the devices

i need quick solution

thanks

This could be happening for a number of reasons. Here are some things you can try to find out why:

This troubleshooting guide applies when a VPN connection has been successfully established to an Ewon, but one or more LAN devices connected to it cannot be reached. It provides steps on how to resolve this issue and reach one’s LAN devices through eCatcher or M2Web. There are a few issues that can contribute to this issue including as a network overlap (IP conflict), eCatcher firewall settings, and the NatItf setting.

APPLICABLE PRODUCTS

  • Ewon Cosy
  • Ewon Flexy
  • eCatcher
  • M2Web

ISSUE / QUESTION / SYMPTOM

LAN devices are connected to the Ewon, but cannot be reached. Pinging them fails with “no route to host”. Trying to connect to a device like an HMI in the browser never loads.

  1. Network overlap
  2. Firewall set too high
  3. NatItf not set appropriately
  4. RTEnIpFwrd disabled
  5. Device not configured for access through M2Web

POSSIBLE CAUSES / ANSWER

  1. Network overlap

When trying to connect through eCatcher, the local network and the Ewon’s LAN should be in different subnets to allow remote access to all the devices connected to the Ewon’s LAN. When there is overlap between these two networks, you will see the following error messages:


Fig 1. Network overlap 1

Fig 2. Network overlap 2

Troubleshooting Steps:
To solve this issue, there are a few options:

  • Make sure the network of the PC running eCatcher and the Ewon’s LAN are in different subnets
  • Change the LAN IP address of the Ewon and its LAN devices
  • Use a different network address to connect the PC to the Internet
  1. Firewall set too high

The firewall setting in eCatcher can be set to different security levels including Standard and High. When High security is selected, only the listed devices under the Ewon’s LAN are reachable by connected users. Therefore if the LAN device being accessed is not declared on eCatcher, it will not be reachable.

Troubleshooting Steps:
To solve this issue, there are two options:

  1. NatItf not set appropriately

The Ewon’s NAT and TF settings affect how devices must be configured to be accessible through the Ewon’s VPN connection. NAT on LAN (Plug’n Route) only requires that LAN devices’ IP addresses are on the Ewon’s subnet. If this setting is changed to NAT and TF on WAN, the LAN devices must also have their gateway IP set to the Ewon’s LAN IP address.

Troubleshooting Steps :
To solve this issue:

  • On a Cosy, connect to the device’s web interface and navigate to Setup → System → Storage → Tabular Edition → Edit COM cfg and search for NatItf. Double click the value to edit, set it to 3 (for Plug’n Route), save, and reboot the Ewon.

Fig 4. Ewon’s web interface: changing NatItf setting on Cosy

  • On Flexy, navigate to Setup → System → Communication → Networking → Routing, then change the “Apply NAT and TF to connection:” dropdown to NAT on LAN (Plug’n Route)

Fig 5. Ewon’s web interface: changing NatItf setting on Flexy
4. #### RTEnIpFwrd disabled

RTEnIpFwrd is a parameter that allows traffic to be routed from the device’s WAN to its LAN, thereby allowing access to LAN devices through the VPN. If it is set to 0, it will be disabled and no access is allowed.

Troubleshooting Steps:
To solve this issue:

  • Connect to the device’s web interface and navigate to Setup → System → Storage → Tabular Edition → Edit COM cfg and search for RtEnIpFwrd. Double click the value to edit, set it to 1, save, and reboot the Ewon.
  • After rebooting, check that the value is now 1. If it isn’t, verify that the Ewon has a WAN port. If every Ethernet port is set to work as a LAN port, RTEnIpFwrd cannot be changed.
  1. Device not configured for access through M2Web

If LAN devices can be reached through eCatcher but not M2Web, there is likely an issue how the devices are configured in eCatcher.

Troubleshooting Steps:
Ensure that M2Web access is enabled in the device’s configuration in eCatcher. Click on the Ewon in eCatcher → Properties → Configure LAN Devices & Firewall, then either select the device from the list and choose Properties or add a new device if it’s not present. At the bottom of the LAN Device popup, ensure “Visible in M2Web” is checked, and that the protocol, port, and home page (if any) are set appropriately.

Actually, just looking at your screenshot, I can see that you have a network overlap.

image

It looks like you are connecting from a network that share’s the same subnet address as your Ewon’s LAN. I generally recommend to set the LAN address to something uncommon, such as 10.147.62.x/24, for example. Usually you will find most VPN addresses are like this for this very reason.

Hi Thanks for your reply.

I did what you have mentioned its still not working.

let me show you all the screen shots

  1. [moved to staff note]
  2. I am not allow to add IP for the HMI with the subnet mask [moved to staff note]

Hi Kyle,

I did following .

  1. Check the Ewon LAN IP
    [moved to staff note]

  2. Check the E Catcher LAN IP
    [moved to staff note]

  3. E Catcher IP SETUP
    [moved to staff note]

  4. [moved to staff note]

  5. My PC LAN IP
    [moved to staff note]

  6. Talk2m E cathcher IP
    [moved to staff note]

Please advise where did i do mistake ?

I still not getting Ping from the PLC